Solid State Relay - Voltage

Discussion in 'Furnaces and their construction' started by Al2O3, Jan 7, 2018.

  1. Al2O3

    Al2O3 Administrator Staff Member Banner Member

    Anyone ever had an SSR leak voltage when not energized? I've noticed a very low level of illumination on an LED indicator light I have on my heating element circuit, so I put meter on it and sure enough, 10-12VAC. When the SSR is energized, it goes to 240vac. I measured the PID drive voltage and just to make sure, I disconnected the control voltage side of the SSR and even in open circuit control voltage I still measure 10-12vac across the load terminals. It's an 80 amp SSR that's only supporting 18 amps at 240vac.

    Best,
    Kelly
     
  2. PatJ

    PatJ Silver

    I am not surprised at the leakage.
    I open the circuit breaker serving my kilns just to be sure there is nothing energized.

    Solid state devices are not perfectly clean in operation, and they do not work like a mechanical relay with an air break; they are more like fuzzy logic, ie: "Off for all practical purposes".

    That is one reason I don't like them, but it is hard to argue with the controllability that they provide an electric kiln/furnace.
     
  3. Negativ3

    Negativ3 Silver

    Kelly, do you have a circuit available?
     
  4. Jason

    Jason Gold

    I do the same....Call me a chicken, but I'd rather change out a tired CB than take a 240 poke.
     
  5. J.Vibert

    J.Vibert Silver

    More traffic here than at AA apparently. I replied there this morning, and having bothered popping in here till now.

    Guess I should just follow the crowd and start using AA as a secondary site.

     
  6. Al2O3

    Al2O3 Administrator Staff Member Banner Member

    Thanks Jay just replied there.

    I’m with ya all on that one. At least my furnace is lift off so even though I do have the coils switched off when I pour, they're at least out of the way if the SSR decides to call an audible.

    -3, I’ll have to see if I can find it. It was hand drawn and not particularly well organized. I actually drew it after I wired it. There’s a lot going on in there. This is the first time I’ve ever used 240vac in a control circuit. Usually I step it down to 24v for safety reasons but space was at a premium. The hour meters, LEDs, panel meter, and start/stop and PiD are all powered by 240vac as is the coil on the main power contactor. There is a separately fused control circuit. The little toggle switches just open the low voltage control circuit to the SSRs from the PiD output.

    Lot's of other examples on web search of those that describe SSRs not actually being fully open. Though I might have a circuit flaw which could still be the case.

    32 Controller.JPG

    34 Inside Controller.JPG

    Best,
    Kelly
     
  7. PatJ

    PatJ Silver

    I just wish I could remember that it is not Vilbert.
    For some reason that is what I see visually; its an automatic hard-wired thing.

    Glad you are here.
     
  8. Peedee

    Peedee Silver

    Triacs or 'SSR' need a draw down or you will get a leakage that will read on the meter, LED loads are to small to 'run off, that leak. Don't stick fingers on anything that is likely to go live is a simple rule. (as my sadly departed mentor taught me, fuse in the pocket)
     
  9. Al2O3

    Al2O3 Administrator Staff Member Banner Member


    I’ve been thinking about my furnace electrical circuit and there are a couple significant things to share. This is US 240vac so there are two legs that are each 120vac to ground. I’m only opening one leg to control the resistive heating elements so one side of the coil is always connected 120vac above ground so that hazard is always present if you come in contact with the heating elements. I did this because I wanted to be able to run the two heating elements independently and didn’t have the real estate for four SSRs. Being able to run the two circuits independently provides finer control at lower operating temperatures. I’m rethinking this decision though and may rewire the power circuit for safety for reasons considering the discussion below.

    Here is the present circuit. The control/instrument circuit is from memory so I may need to double check all that.

    Present Electrical Scematic.jpg

    Here is the reconfiguration of the power circuit I’m considering. Basically re-wire the two heating elements in parallel and isolate each side of the element with one of the two existing SSRs. I’ll lose the ability to operate them independently but when the SSRs are open, there will be no voltage on the coils…..as long as the SSRs don’t leak current/voltage. It will double the current through each SSR from 18A to 36A but they are rated at 80A.

    Proposed Ckt Revision.jpg

    In the present configuration it’s also true that one side of the LED and power meters are always connected to one leg of the 240vac, 120vac above ground, but not grounded so possible that the voltage I measured is the 120vac dropping across the heating coil and somehow finding ground down stream of the LED. The control box, control box door, furnace body, and chassis are all grounded back to Earth ground.

    Over the holidays just before the furnace fail, I did several indoor melts. It was warm in my shop and I was in shirt sleeves. Several times when I was using my carbon sheathed pyrometer to measure molten metal temperature I got a low voltage shock from the braided sheath of my K-Thermocouple when the inside of my arm came in contact with it. I couldn’t find the source but think I now know what caused it. I believe one of the coils that had been damaged and repaired may have been out of its groove and contact the graphite crucible. From there the circuit was completed through the molten aluminum, to the carbon pyrometer sheath, and then to the Inconel sheath of the grounded TC, and of course onto the metal over-braid I was contacting. I don’t recall whether it was the top side or bottom side of the coil that continuously tied to one leg of the 240vac source what I may have been feeling was 120vac dropped through some length of the ohm coil. I’m somewhat surprised this didn’t smoke my PiD with voltage on the TC input. But it was what got me more interested in scrutinizing the circuit before the rebuild was complete.

    Also, I noticed the SSR manufacturer specifies <=2mA off leakage current.

    What to you all think about the above and the proposed change? Go easy on me fellas, electrical and wiring diagrams are not a strength of mine.

    Best,
    Kelly
     
  10. Negativ3

    Negativ3 Silver

    How much current does your meter show with the circuit in the open position?

    Disconnecting both 110V phases is a good idea.

    Travelling now. Will respond in detail when home.
     
  11. Al2O3

    Al2O3 Administrator Staff Member Banner Member

    I'll need to measure the current.

    The manufacturer spec sheet says less than 2mA but elsewhere in there literature is says it can be up to 30mA for the bigger capacity relays. Deeper in the FAQs it indicates the leakage is sufficient to power small buzzers and LEDs. Might like some advice on if/how to bleed that off, but suppose that's why you'd like to know what the leakage current measures.

    Best,
    Kelly
     
  12. PatJ

    PatJ Silver

    I remember looking at a lot of wiring diagrams when I was setting up my kiln controller, and reading a lot about the in's and out's of various arrangements online with single and dual SCR's, but now I forget what I discovered.

    I can say that in general, I don't like to mix my power circuits with my control circuits, ie: I would have one 2-pole breaker for powering the SCR's and another 1-pole breaker for controls only, but again I need to go check how I set mine up because I don't recall using two breakers.
    I don't like having the possibility of getting feedback through anything.

    I will try and dig that stuff out and post it.

    Edit:
    Here is some online info I found:
    https://www.phidgets.com/docs/Solid_State_Relay_Primer

    https://en.wikipedia.org/wiki/Solid-state_relay


    As I recall, the controller is just switching the SSR on and off quickly at varying rates to control the power flowing to the load.
     
    Last edited: Jan 8, 2018
  13. PatJ

    PatJ Silver

    I found the sketches I made for my kiln controller hookup.
    I remember playing around with the controller and putting it on the scope, but I don't think I have actually run it on the kilns yet.

    I looked up several heating element controller wiring diagrams, and I don't see the need for two SSR's unless you are using a 3-phase power source, or perhaps if one SSR cannot handle the entire load.

    But why use two SSR's when one works?
    Seems like I have read some doomsday posts on other forums about the need for using two SSR's always, but I don't believe it, or rather have no reason to believe that one SSR would not work safely and well.

    Below are some photos of the equipment I bought (I also bought a beefy heat sink for the SSR), the instructions, and my wiring diagram sketches (un-tested, use at your own risk).
    And be aware that wiring diagrams vary greatly depending on the exact equipment you are using. There is no single wiring diagram for SSR heating element controls that works in all situations.

    The instructions are written in Chinenglish; so a bit of a challenge to interpret (the price was right).

    And there are some meltdown/burnup photos on the net of SSR's, so perhaps not a good idea to leave them unattended.
    As I mentioned above, I open the two-pole breaker serving the kiln when I am not using it.

    And as I recalled above, I do use a separate 120 volt breaker to feed control power, so that I don't get any feedback from tapping one line of a 240 volt circuit.
    I always use a separate 120 volt control source unless I am using a control power transformer on a 3-phase circuit, but you need labels to warn that both breakers must be turned off to safely work on the equipment if you choose to use a separately derived control power source.

    Edit:
    Don't ask me what the waveform means; I was just playing around with it and I assume that is a junk signal of some type, or maybe that is the output, and it is showing some clipping.


    Document (234).jpg

    Document (265).jpg

    Document (266).jpg

    Document (267).jpg

    FOTEK-SSR-100-DA.jpg

    MYPIN-T-SERIES-CONTROLLER-01.jpg

    MYPIN-T-SERIES-CONTROLLER-02.jpg

    MYPIN-T-SERIES-CONTROLLER-03.jpg

    THERMOCOUPLE-TYPE-K.jpg

    rImg_0126.jpg

    rImg_0127.jpg

    rImg_0131.jpg

    rImg_0133.jpg
     
    Last edited: Jan 8, 2018
  14. Al2O3

    Al2O3 Administrator Staff Member Banner Member

    Like I mentioned in the post, two reasons:
    1. I have two elements that I want to be able to operate independently for two power levels, one or both powered. I could run both in parallel with one SSR without the ability to run each heater circuit independently, but......
    2. US 240vac is 240 between legs but 120vac from each leg to ground. If you don't open each side of the heating element the coil will always be 120v to ground and if you contact the coil and are grounded that's the potential shock you could receive. You cant open both sides of the heating element without two relays.
    Best,
    Kelly
     
  15. PatJ

    PatJ Silver

    I understand about independent control. I don't see a problem with doing that.

    But if I understand you correctly, it is as if you want to be able to have physical contact with a coil (either an accidental touch, or perhaps contact with metal lifting tongs, etc) while the SSR circuit is on, but with the SSR in its non-conductive (low-conductive) state?

    I would not reach into a kiln with the power on, whether the SSR was conducting or not.
    If I had to reach into a kiln, I would either open the 2-pole circuit breaker feeding the kiln, open a wall-mounted disconnect switch, or if I am going to work on the unit, unplug it from the 240 volt receptacle and turn off the 120 volt control circuit.

    You could use your main contactor to turn off 240 volt power to the unit, but contactor contacts can weld closed, and there is no guarantee that they will actually open when you think they are open.

    So I guess I don't see why you could not just turn off the 240 before opening the furnace?
    I suppose I don't understand your operation exactly.
     
  16. Negativ3

    Negativ3 Silver

    I am very familiar using single-phase 240V in the UK for as many years, and a single line being "hot" is the norm for me. Neutral in my experience has always been at 0V potential.
    USA seems to have the Neutral being the center tap of the utility transformer, with the two split-phase 120V hots 180 degrees out of phase with each other, giving 240V. The Neutral is only used if 120V is required. The Neutral is not used if 240V service is needed. Safety Earth must be used in all cases.

    Isolation of power to Kelly's heating coils is the objective, with a means of reducing leakage current to a minimum.

    I will be testing my setup which uses the same SSR to a resistive heating element. If an SSR is not isolating power sufficiently to make it safe, another means of powering the coils should be investigated i.e. ye olde contactors.
     
    Last edited: Jan 9, 2018
    Hopefuldave likes this.
  17. Negativ3

    Negativ3 Silver

    If you need to keep power to the rest of your system while handling material in/out of the furnace bore (temperature?), I would go for a three-pole isolator between the SSR output(s), both split-phases and the heating element connections.

    In the nature of KISS, it does require you to make it safe each time, but it allows you to keep your independent control.

    [​IMG]

    Randomly got this 4-pole one from Amazon UK...

    https://www.amazon.co.uk/Gewiss-GW70436-Rotary-Isolator-Neutral/dp/B008OQLOO8

    Space depending of course.
     
  18. Negativ3

    Negativ3 Silver

    Small error in the last circuit which would have isolated everything. Now corrected.

    [​IMG]
    [​IMG]
    Phew!
     
  19. PatJ

    PatJ Silver

    Seems like in your second diagram, if you touched he left side of either coil/hour meter connection, you could complete the circuit to ground and get 120 VAC.
     
  20. Negativ3

    Negativ3 Silver

    Pat,

    Agreed however those connections should be in the control cabinet and not in the furnace bore.
     